We have a large building that is served by the utility with a 13.2KV primary. We have 15KV switchgear and a number of unit substations around the structure. Pretty straight forward. But...
In a couple of cases there was no room for an interior substation so primary MV conductors were run out of the building to pad-mount switch gear and pad-mount transformers. Secondary conductors then come from the transformers back into the building and terminate in 480 or 208 switchboards.
As far as bonding should those secondaries be treated as service entrance conductors, separately derived systems, or feeding one structure from another?
In the case of serivce entrance there would be no grounds run with the secondary and we would have a main bonding jumper in the switchboard.
In the case of a separately derived system we would normally have the option of making the bonding jumper in the transformer or in the first disconnect. In this case the pad-mounts are typically bonded and we would need to pull grounds in with the secondary and not have bonding jumpers installed in the switchboards .
In the case of feeding one structure from another we would run the equipment grounding conductors with the secondary and not have bonding jumpers in the switchboards.
Any words of wisdom appreciated.
We have a large building that is served by the utility with a 13.2KV primary. We have 15KV switchgear and a number of unit substations around the structure. Pretty straight forward. But...
In a couple of cases there was no room for an interior substation so primary MV conductors were run out of the building to pad-mount switch gear and pad-mount transformers. Secondary conductors then come from the transformers back into the building and terminate in 480 or 208 switchboards.
As far as bonding should those secondaries be treated as service entrance conductors, separately derived systems, or feeding one structure from another?
In the case of serivce entrance there would be no grounds run with the secondary and we would have a main bonding jumper in the switchboard.
In the case of a separately derived system we would normally have the option of making the bonding jumper in the transformer or in the first disconnect. In this case the pad-mounts are typically bonded and we would need to pull grounds in with the secondary and not have bonding jumpers installed in the switchboards .
In the case of feeding one structure from another we would run the equipment grounding conductors with the secondary and not have bonding jumpers in the switchboards.
Any words of wisdom appreciated.