JGenette7132
Member
- Location
- harrisontownshipmi
- Occupation
- Electrical Inspector
I have one existing structure 240.000sq ft and a 3hour firewall creating 2 buildings with separate addresses on one property.
bldg. one has a 1600 amp 120/240 volt three phase overhead service, Building two has two separate services a 1200 amp 120/240 volt
three phase and a 277/480 volt three phase service. The empty bldg. was being renovated, during which time a correctly listed fire
rated overhead door and a listed man door were installed in the fire wall. I felt the rating on the wall was compromised and that it
was now one building with 3 services and had to be reviewed by a DTE service planner (who had no problem with the services, but I could
make them install one service if I wanted per 2023 NEC 230-2). Another suggestion I got was to install signage on doors saying " Doors
must be closed when occupied. Is this still 2 separate buildings or one building