florida-sparkey
- Pinellas Park, Florida
- Master Electrician
Hello and thank you!
I am installing an auxiliary gutter that has two parallel risers with each containing 4- 250KCM AL wires (3P 400A service)
Each RMC will be threaded into a myers hub.
Question. Is a bonding jumper required? I will cut my own holes and a myers hub does not rely on a "standard locknut" 250.92(B) or so I think. Clearly I may be wrong.
If needed This becomes the bonding jumper question.
I planned on bonding each riser with an individual #4 CU jumper wire per 250.102(2) using a meg bushing
I will install a ground block solidly bolted to gutter and bond the 2 neutrals and 2 bonding jumpers (if required) here for service side bonding.
I am totally confused as to what table 250.120(C)(1) note 2 is saying.
Can someone tell me in English because 10 rereads did not clear it up for me. Do I need to change the size of the bond wire or change it to #2 AL to meet the notes requirement?