Service size calculation
mshields
Boston, MA
Doing a service size calc and I've got a substantial amount of electric heat (in the form of Terminal Boxes). Because Article 424.3 which is referenced by Table 220.3, states that this is a continuous load, I'm taking this load at 100%.
Is that correct?
Thanks,
Mike
I think you are both right, for different parts of the calculation.
Section 424.3 is for branch circuits. Sub-section 'B' states that the equipment shall be considered a continuous load- for calculating branch circuits.
Thus, 125% of the nameplate while figuring each and every branch circuit.
Then when calculating feeder and service loads, Section 220.51 allows the load to be calculated at 100%, as long as not smaller than the largest branch circuit.