Southern Charm
Member
- Location
- New Jersey
- Occupation
- Service Technician
If you built a 400 amp residential service wouldn’t the conductors between the utility point of attachment ( overhead ) and the meter enclosure need to be a minimum of 400 copper or 600 Al. ? Then if you wanted to go from the load side of the meter ( double lugs ) to two 200 amp disconnects with say 4/0 Al to each panel that would be fine. Co worker told me the line side meter wire is decided by a load calculation. I say no, it’s decided by the OCPD. Another example, if you had an 800 amp commercial service with 4 disconnects at 200 amps each you could parallel two sets of 500 copper. I’m I missing something?