We are wiring a 2300sq.ft. home and are installing 200amp service. The distance from the meter base to the pole is 250' and the distance from the meter base to the panel is 40'. We have approx. the load at 160 amps and will be installing 3-3/0 thhn cu conductors in 2" schedule 80 pvc. We have calculated the VD at 7.18 which is 2.99%. We also will be installing a 100 amp sub panel in a barn at 70' with a load of approx. 50 amps with 3-#6 thhn cu conductors in 1.25" pvc schedule 80. We have calculated the VD at 3.43 which is 2.86%. Are we correct in our calculations?