Service Size

Status
Not open for further replies.

Designer69

Senior Member
I have come up with 345A of demand load for a new 120/240 1-ph service.

Can I get by with a 400A service or do I need 500A? IE- if the main breaker is supposed to be loaded to 80% then 320A would be the max. my demand amps should come to.

Thanks
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Is this a residence. Then it is not an issue. If the loads are continuous at 345 then you would use an 80% calculation and there would be a problem.

Is the demand load the calculated load or the real time measurement?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The calculated load is used to determine the service size. If it's 400 amps you need a minimum 400 amp service.
 

Designer69

Senior Member
The calculated load is used to determine the service size. If it's 400 amps you need a minimum 400 amp service.

thank you. My calculated load came in at exactly 345 amps.

does this mean I don't need to apply any other multiplication like 1.25 to the 345A or make sure the calculated load doesn't come in at a max 320A for a 400A service (400 x 80% = 320)?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
thank you. My calculated load came in at exactly 345 amps.

does this mean I don't need to apply any other multiplication like 1.25 to the 345A or make sure the calculated load doesn't come in at a max 320A for a 400A service (400 x 80% = 320)?

You already did the calc, 345 amps is the minimum service size.
 

kwired

Electron manager
Location
NE Nebraska
If you have a single 400 amp overcurrent device for service disconnect - you must supply it with 400 amp conductor.

If you had two to six service disconnecting means grouped in one location - say they were all 100 amp, and a load calculation of 345 - your common service conductor only needs to have an ampacity of 345.
 

packersparky

Senior Member
Location
Wisconsin
Occupation
Inspector
If you have a single 400 amp overcurrent device for service disconnect - you must supply it with 400 amp conductor.

If you had two to six service disconnecting means grouped in one location - say they were all 100 amp, and a load calculation of 345 - your common service conductor only needs to have an ampacity of 345.

I think he could use 500 kcmil copper (380 amps) and use a 400 ampere overcurrent device per 240.4(B).
 

kwired

Electron manager
Location
NE Nebraska
I think he could use 500 kcmil copper (380 amps) and use a 400 ampere overcurrent device per 240.4(B).
To a single OCPD yes. What I was getting at is for multiple service disconnecting means, a common supply conductor only needs to be sized to calculated load. He could have six 100 amp breakers for service disconnecting means - but only required to have 345 amps of service conductor. If he hits a splice box or gutter he needs 100 amp conductor to each individual overcurrent device though.
 