I have an agricultural application where a service is required for 2 machines, each with 320 hp connected load at 480 volt, 3 phase.
From 220.102 - all load are expected to operate simultaneously.
Full load is:
361A x 2 = 722 A
14A X 2 = 28A
Total connected load = 750A .... so a 800 amp service should be enough as per table 220.102 (100%) ?