I have a disagreement with an engineer regarding my service calculations. The project is a small physical therapy suite. I come up with 188 A for my service over current protection and 3/0 for a feeder size.
The engineer wants me to put a 225-A panel boar in and 4/0 feeders because he considers the RTU (s) which are A/C gas fired heat to be a continues load. And that ?a panelboard may only be loaded to 80% of its rating?. He actually says that ?all equipment may only have 80% connected load of its rating?. Like a disconnect for instance ?many only have a circuit which has up to an 80-amp load?.
SQ. FT. 4247
NON CONTINUOUS LOADS
NEC RECEPTACLE LOADS QTY. Total VA
220.44 Receptacles at 180VA 56 10080
NEC Specific Applaiances or Loads QTY. Total VA
220.14 (A) Tread Mills at 1800VA 6 10800
Elliptical/Cross Trainers at 180 6 1080
Hot Packs at 1200 2 2400
Microwave at 1800 VA 1 1800
Refrigerator at 1800 VA 1 1800
Water Heater Power Vent at 360 1 360
220.52 (B) Washer Recpt at 1800 VA 1 1500
220.54 Dryer Recpt. At 5000VA 1 5000
Total 34820
NEC Demand Factors - Non Dwelling Recpt. Loads
Table 220.44 First 10 KVA 100% 10000 10000
Remainder Over 10KVA 50% 24820 12410
Sub Total Non Continuous 12410
CONTINUOUS LOADS
Table 220.12 General Lighting 3.5 VA per Sq Ft 4247 14864.5 * See Note
220.14 (F) Outside Sign Circuit at 1200 VA 1 1200
Sub Total Continuous 16064.5
OTHER NONCONTINUOUS LOADS
Water Heater at 1800 VA 1 1800
RTU #1 1 12248
RTU #2 1 12248
220.51 Wall Heatrer at 3000VA 3 9000
Sub Total Other Non Continuous 35296
* Note Actual lighting load is less than the load from table 220.12 so the minimum lighting load from table 220,12 is used in the calculation.
Sub Total Non Continuous 12410
Sub Total Continuous 16064.5
Sub Total Other Non Continuous 35296
Total Continuous + Non Continuous Loads 63770.5
MINIMUM SIZE FEEDER (OR SERVICE) OVERCURRENT PROTECTION 215.3 OR 230.90
Sub Total Non Continuous 12410
Sub Total Other Non Continuous 35296
Sub Total Continuous at 125% 20080.625
Total 67786.625
67786 VA / 208 V / 1.732 = 188 A
See 240.6 The Next Higher Standard size is 200-A
MINIMUM SIZE FEEDER (OR SERVICE CONDUCTORS) 215.2 & 230.42 (A)
67786 VA / 208 V / 1.732 = 188 A
215.3 & 310.16 Service or feeder Conductor is 3/0
All Calculation shown above are take from example "D3 Store Building" in Annex D of the 2005 NEC
Thanks,
Mike
The engineer wants me to put a 225-A panel boar in and 4/0 feeders because he considers the RTU (s) which are A/C gas fired heat to be a continues load. And that ?a panelboard may only be loaded to 80% of its rating?. He actually says that ?all equipment may only have 80% connected load of its rating?. Like a disconnect for instance ?many only have a circuit which has up to an 80-amp load?.
SQ. FT. 4247
NON CONTINUOUS LOADS
NEC RECEPTACLE LOADS QTY. Total VA
220.44 Receptacles at 180VA 56 10080
NEC Specific Applaiances or Loads QTY. Total VA
220.14 (A) Tread Mills at 1800VA 6 10800
Elliptical/Cross Trainers at 180 6 1080
Hot Packs at 1200 2 2400
Microwave at 1800 VA 1 1800
Refrigerator at 1800 VA 1 1800
Water Heater Power Vent at 360 1 360
220.52 (B) Washer Recpt at 1800 VA 1 1500
220.54 Dryer Recpt. At 5000VA 1 5000
Total 34820
NEC Demand Factors - Non Dwelling Recpt. Loads
Table 220.44 First 10 KVA 100% 10000 10000
Remainder Over 10KVA 50% 24820 12410
Sub Total Non Continuous 12410
CONTINUOUS LOADS
Table 220.12 General Lighting 3.5 VA per Sq Ft 4247 14864.5 * See Note
220.14 (F) Outside Sign Circuit at 1200 VA 1 1200
Sub Total Continuous 16064.5
OTHER NONCONTINUOUS LOADS
Water Heater at 1800 VA 1 1800
RTU #1 1 12248
RTU #2 1 12248
220.51 Wall Heatrer at 3000VA 3 9000
Sub Total Other Non Continuous 35296
* Note Actual lighting load is less than the load from table 220.12 so the minimum lighting load from table 220,12 is used in the calculation.
Sub Total Non Continuous 12410
Sub Total Continuous 16064.5
Sub Total Other Non Continuous 35296
Total Continuous + Non Continuous Loads 63770.5
MINIMUM SIZE FEEDER (OR SERVICE) OVERCURRENT PROTECTION 215.3 OR 230.90
Sub Total Non Continuous 12410
Sub Total Other Non Continuous 35296
Sub Total Continuous at 125% 20080.625
Total 67786.625
67786 VA / 208 V / 1.732 = 188 A
See 240.6 The Next Higher Standard size is 200-A
MINIMUM SIZE FEEDER (OR SERVICE CONDUCTORS) 215.2 & 230.42 (A)
67786 VA / 208 V / 1.732 = 188 A
215.3 & 310.16 Service or feeder Conductor is 3/0
All Calculation shown above are take from example "D3 Store Building" in Annex D of the 2005 NEC
Thanks,
Mike