Service switch

Merry Christmas
Status
Not open for further replies.

PaulEd

Member
Location
United States
For the new service switch required for services and service changes on the outside of a house. It’s my understanding that we don’t need to bond the ground rod and Watermain at the switch on the outside but we could still do it at the panel on the inside? Wasn’t there an exception in the code that allowed for the switch outside to not be the main switch therefore not requiring a neutral/ground bond?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
IMO, it's a word game.
If you call it a "service switch" ie: service disconnect the the GEC would connect there (or before)
If you call it an "Emergency Disconnect" per 230.85 then the GECs could connect to your Service Disconnect.
 

PaulEd

Member
Location
United States
IMO, it's a word game.
If you call it a "service switch" ie: service disconnect the the GEC would connect there (or before)
If you call it an "Emergency Disconnect" per 230.85 then the GECs could connect to your Service Disconnect.
Any experience on what the AHJ’s are calling it?
 

marmathsen

Senior Member
Location
Seattle, Washington ...ish
Occupation
Electrical Contractor
I have been meaning to ask the same question. If you simply label the ESD as "EMERGENCY DISCONNECT, NOT SERVICE EQUIPMENT" does that give you the ability to have the GES run to the indoor panel with a main disconnect labeled "SERVICE DISCONNECT"? This would be a big labor saving trick when doing a service change where the existing electrode system is OK to reuse.

Rob G, Seattle
 
IMO, it's a word game.
If you call it a "service switch" ie: service disconnect the the GEC would connect there (or before)
If you call it an "Emergency Disconnect" per 230.85 then the GECs could connect to your Service Disconnect.
I have been meaning to ask the same question. If you simply label the ESD as "EMERGENCY DISCONNECT, NOT SERVICE EQUIPMENT" does that give you the ability to have the GES run to the indoor panel with a main disconnect labeled "SERVICE DISCONNECT"? This would be a big labor saving trick when doing a service change where the existing electrode system is OK to reuse.

Rob G, Seattle


But doesnt it depend on the wiring betwix the outside disconnect and the inside disconnect?

IF it is 3 wire betwix, then you cannot call the outdoor thing a service disconnect.
If it is 4 wire betwix, then the outside thing is your service disconnect (could you elect to not use one of the conductors and then go to case #1?)

BTW though, note the GEC can terminate anywhere from the service point to the service disconnect. IT does not have to be in the service disconnect.
 

marmathsen

Senior Member
Location
Seattle, Washington ...ish
Occupation
Electrical Contractor
But doesnt it depend on the wiring betwix the outside disconnect and the inside disconnect?

IF it is 3 wire betwix, then you cannot call the outdoor thing a service disconnect.
If it is 4 wire betwix, then the outside thing is your service disconnect (could you elect to not use one of the conductors and then go to case #1?)

BTW though, note the GEC can terminate anywhere from the service point to the service disconnect. IT does not have to be in the service disconnect.

But doesnt it depend on the wiring betwix the outside disconnect and the inside disconnect?

IF it is 3 wire betwixt, then you cannot call the outdoor thing a service disconnect.
If it is 4 wire betwixt, then the outside thing is your service disconnect (could you elect to not use one of the conductors and then go to case #1?)

Yes I didn't include the bit of detail about not having an equipment ground but that would be part and parcel of having the service disconnect inside and not at the emergency service disconnect.


BTW though, note the GEC can terminate anywhere from the service point to the service disconnect. IT does not have to be in the service disconnect.

True, but I was trying to figure out if it was allowed to leave the GEC at the indoor panel when doing a service/panel change

Rob G, Seattle
 
Yes I didn't include the bit of detail about not having an equipment ground but that would be part and parcel of having the service disconnect inside and not at the emergency service disconnect.




True, but I was trying to figure out if it was allowed to leave the GEC at the indoor panel when doing a service/panel change

Rob G, Seattle
If you only have three wire between the inside and outside disco, I don't see how you can call the outside one a service disconnect unless you replaced the cable to 4 wire. So your inside disco is your service disco and you can certainly land your GEC there.
 

marmathsen

Senior Member
Location
Seattle, Washington ...ish
Occupation
Electrical Contractor
If you only have three wire between the inside and outside disco, I don't see how you can call the outside one a service disconnect unless you replaced the cable to 4 wire. So your inside disco is your service disco and you can certainly land your GEC there.
Is anyone else using this trick when doing service changes? If so have you had pushback from AHJs?

Rob G, Seattle
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Wasn’t there an exception in the code that allowed for the switch outside to not be the main switch therefore not requiring a neutral/ground bond?
Depends on code cycle you are on. Assume your reference to "the main switch" is actually the first overcurrent devise.
The "switch" can be a simple blade type or be a breaker style with the allowance found beginning with the '20 cycle of a "Label" applied with wording difference found in @augie47 reference above.
 