I have a somewhat-unusual setup, or at least one that I haven't encountered before. An outdoor service transformer has three circuit breakers within a enclosure that is shared with the transformer, and that is located on the same pad. That is, if you open doors on one side you see the transformer. If you open doors on the other side you see the breakers. Two of the breakers are small, and serve outdoor lights and a small picnic area. The third is much larger, and provides power to a main distribution panel inside the building. I put the N-G bond inside the outdoor enclosure, attached the GEC to the neutral bar, and ran an EGC with the conductors to the indoor panel. A client engineer who is reviewing the package is telling me that the N-G bond belongs inside the indoor panel, and that the GEC should run from there to the ground bar with the electric room. To my way of thinking, the “service disconnecting means” mentioned in 250.24(A)(1) is the breaker that sits two feet away from the transformer. My problem is the terminology: that same sentence speaks of “service drop” and “service lateral,” neither of which appears to apply to my situation. Any thoughts?