arc_flashed
Member
- Location
- FL, United States
I am hoping someone can help clarify the requirements for grounding an electrical service. I've come across an install that needs a secondary customer owned transformer to step down the voltage from the utility transformer and I am having a hard time getting my ground sizes and terminology together.
The utility transformer has a secondary voltage of 480/277vac. Customer needs 120/208 so a step down transformer will be installed. This transformer doesn't need a neutral on the primary, so I haven't planned on pulling one from the utility, but supply side bonding jumper should still be pulled correct? This would be connected to the utility transformer ground, no the X0?
Then my step down transformer will have both a SSBJ and a neutral conductor with the bonding occurring in the first means of disconnect.
I've attached a drawing of my system and what I believe the correct grounding and terminology is but I do not have a lot of experience with new services.
Any help is greatly appreciated.
The utility transformer has a secondary voltage of 480/277vac. Customer needs 120/208 so a step down transformer will be installed. This transformer doesn't need a neutral on the primary, so I haven't planned on pulling one from the utility, but supply side bonding jumper should still be pulled correct? This would be connected to the utility transformer ground, no the X0?
Then my step down transformer will have both a SSBJ and a neutral conductor with the bonding occurring in the first means of disconnect.
I've attached a drawing of my system and what I believe the correct grounding and terminology is but I do not have a lot of experience with new services.
Any help is greatly appreciated.