Please see attached sketch. I have 480/277V three phase incoming electric utility service conductors into trough 3 sets of 4#600kcmil. From trough there are three connections in metallic conduit to three service disconnects.
From trough to SVRC#1: Fused at 400A incoming I have 3#500kcmil phase conductors + 1#500 kcmil neutral
From trough to SVRC#2: Fused at 200A incoming I have 3#3/0Awg phase conductors + 1#3/0 Awg neutral
From trough to SVR#3: Fused at 600A incoming I have 3 sets of 3#3/0 phase conductors + 1#3/0 neutral
Question:
1. Since their is no equipment groundconductor coming in line side of fused disconnects how would the wireway, metallic conduit between trough and service disco and service disconnects themself be grounded and bonded? They are metallic.
2. Would the same question as number #1 however the incoming utility voltage is 208/120V three phase?
From trough to SVRC#1: Fused at 400A incoming I have 3#500kcmil phase conductors + 1#500 kcmil neutral
From trough to SVRC#2: Fused at 200A incoming I have 3#3/0Awg phase conductors + 1#3/0 Awg neutral
From trough to SVR#3: Fused at 600A incoming I have 3 sets of 3#3/0 phase conductors + 1#3/0 neutral
Question:
1. Since their is no equipment groundconductor coming in line side of fused disconnects how would the wireway, metallic conduit between trough and service disco and service disconnects themself be grounded and bonded? They are metallic.
2. Would the same question as number #1 however the incoming utility voltage is 208/120V three phase?