beerbelly25
Member
- Location
- OHIO USA
- Occupation
- Electrician
This subject has been covered fairly well in previous posts, but I'm looking for absolute clarity with regard to neutral and ground separation at the existing (old main panel) during conversion to a sub panel. I had to relocate my main service due to an addition that created clearance problems with the overhead service entrance conductors. I placed a new 200A meter/panel combo in another location on the side of the house and fed aluminum 2-2-2-4 to the existing (old main panel) with a 90A breaker in the new 200A panel. The existing (old main panel) is a Crouse-Hinds 150A and I ordered and installed a separate ground bar made by Siemens/Eaton who apparently now owns the C-H brand. I separated all of the neutral and grounds and ran a temporary #6 stranded copper jumper between the grounds and neutrals to use until the new service goes live. The neutral bus bar is insulated with plastic offsets at the base and a cardboard insulator that extends up to the side of the box to prevent the neutrals from touching the bare metal enclosure and making ground contact. I can't determine if this old panel has a neutral bonding screw. The inspector has passed all of my work on the new 200A panel and is now requiring me to disconnect the neutral wire on the old main panel and the temporary jumper to check for continuity between the ground and neutral bus bars. There are 2 existing grounds on the old main panel that were formerly attached to the neutral bus bar. I relocated those to the newly installed ground bar per the inspectors requirements, but from reading these forums, I feel that these grounds should be removed from the new ground bar in the sub panel (one is a #6 solid copper water line ground and the other is a from a ground rod via #4 stranded aluminum) when the new service goes live because the new 200A main panel has 2 of its own ground rods and is feeding the ground (#4) to the converted sub panel via the 2-2-2-(#4) wire.
Questions:
https://postimg.cc/gallery/7wKhHct
Questions:
- Should the 2 ground wires (from water line and old existing ground rod) be removed from the ground bar on the old main panel after it’s fully converted to a sub panel? There seems to be disagreement on the forums here. The inspector is wanting me to leave these ground wires attached on the newly installed ground bar in the converted sub panel even though a ground is fed from the new panel via the 2-2-2-4 feeder. Should I tell the inspector that this is incorrect?
- The inspector wants me to shut off the main breaker on the panel we are converting to the sub panel and remove the neutral wire from what is currently the service entrance cable from the neutral lug and remove my temporary jumper going from neutral to the ground and take of a video of me checking for continuity between the neutral and ground bars. This is in order for me to make sure that the neutral is completely isolated on the old panel before conversion to a sub panel.
- I don’t see a bonding screw on the neutral bar in my old C-H panel. Has anyone worked on the older C-H panels? Is there a bonding screw and if so, where would it be located? When I check for continuity between ground and neutral the existence of a bonding screw should become apparent, but I'd like to know the location of this screw if it needs removed. I’m including photos of the old 150A main panel that is being converted to a sub panel below for your reference.
https://postimg.cc/gallery/7wKhHct