haywire
Member
- Location
- Milpitas, ca
- Occupation
- Electrician
Not sure about new code requirements for meter main upgrades. It's 100 amp zinsco panel 15 circuits upgrading to 125 amp am I right with a #3 thhn and 1 1/2" riser?
I don’t believe so. #3 Thhn copper has an ampacity of 100amperes.Not sure about new code requirements for meter main upgrades. It's 100 amp zinsco panel 15 circuits upgrading to 125 amp am I right with a #3 thhn and 1 1/2" riser?