We’ll there is a pipe for the well which is why I’m confused. When we have a water meter we have to hit the street side first then then secondary side correct!?If there is no metal water pipe that qualifies as an electrode all you need are two ground rods for the GES.
If there is a metal water pipe for the well does that have to be hit or is the rod enoughIf there is no metal water pipe that qualifies as an electrode all you need are two ground rods for the GES.
(1) At least one structural metal member that is in direct contact with the earth for 3.0 m (10 ft) or more, with or without concrete encasementRead 250.52(A)(1)
Where do you see the words "one structural member" in (A)(1)(1) At least one structural metal member that is in direct contact with the earth for 3.0 m (10 ft) or more, with or without concrete encasement
That still does not tell if it has to be hit. And where
(A) Electrodes Permitted for Grounding.
(1) Metal Underground Water Pipe. A metal underground
water pipe in direct contact with the earth for 3.0 m (10 ft) or
more (including any metal well casing bonded to the pipe) and
electrically continuous (or made electrically continuous by
bonding around insulating joints or insulating pipe) to the
points of connection of the grounding electrode conductor and
the bonding conductor(s) or jumper(s), if installed.
I am not a professional at interpreting the words in this book sorry sir.Where do you see the words "one structural member" in (A)(1)
And yes, if it is present it has to be used.
That you for the detailed response that’s exactly what I was looking for. The help is greatly appreciatedIf there is a metal water pipe from the well and there is 10' of contact with the earth then that pipe would be an electrode and must be connected to the grounding electrode system within 5' of where it enters the building. If there is a meter under the house then you need to run a jumper between both sides of the water line.
If the pipe from the well is plastic and the rest of the house is metal then you need to bond the metal piping at any point along the pipe.
Your profile says you are an electrician. Regardless, you do not have to interpret the words of 250.50(A)(1) they are straight forward, you were reading 250.52 (A)(2)(1)I am not a professional at interpreting the words in this book sorry sir.
Yea I am, so that means I’m supposed to be able to interpret everything in the book with out having questions!?….. I’m here to ask and learn to do the job correctly and safe. I’m not perfect and would never claim to be. IYour profile says you are an electrician. Regardless, you do not have to interpret the words of 250.50(A)(1) they are straight forward, you were reading 250.50 (A)(2)(1)
Questions are fine and good but I gave you the article section and you didn't read it, you read another section.Yea I am, so that means I’m supposed to be able to interpret everything in the book with out having questions!?….. I’m here to ask and learn to do the job correctly and safe. I’m not perfect and would never claim to be. I
Thanks I’ll read it up and down when I get to my book.Questions are fine and good but I gave you the article section and you didn't read it, you read another section.
Thanks I’ll read it up and down when I get to my book.