Trovmar said:Hi guys, quick question i was told today that you can only use schedule 80 pvc conduit for a service to a one family dwelling. He proceeded to tell me that if i use schedule 40 pvc i will fail inspection. Is this true?:-?
I have seen guys spin the writing around when they bought the wrong pipe to make it not as obvious.Trovmar said:Hi guys, quick question i was told today that you can only use schedule 80 pvc conduit for a service to a one family dwelling. He proceeded to tell me that if i use schedule 40 pvc i will fail inspection. Is this true?:-?
Trovmar said:Hi guys, quick question i was told today that you can only use schedule 80 pvc conduit for a service to a one family dwelling. He proceeded to tell me that if i use schedule 40 pvc i will fail inspection. Is this true?:-?
quogueelectric said:I have seen guys spin the writing around when they bought the wrong pipe to make it not as obvious.
Trovmar said:Hi guys, quick question i was told today that you can only use schedule 80 pvc conduit for a service to a one family dwelling. He proceeded to tell me that if i use schedule 40 pvc i will fail inspection. Is this true?:-?
don_resqcapt19 said:This is always a call by the inspector. Schedule 40 cannot be used where subject to physical damage. That is a very subjective rule. 352.10(F)
abe72487 said:I usually require SCH 80 where the conductors are unfused and SCH 40 when it is fused. However check with local AHJ for specifics.
That is ok as long at the conduit is on the line side of the service point. The utility has no right to make rules for anything, other than their meter, that is on the load side of the service point.bikeindy said:Here it is required by the POCO
Chamuit said:Were aren't allowed to use Sch40 here at all for service risers.
One POCO will allow Sch80 risers, the other requires Steel Risers only.
Chamuit said:Were aren't allowed to use Sch40 here at all for service risers.
One POCO will allow Sch80 risers, the other requires Steel Risers only.