This may sound like a silly question but i have to ask it anyway. Recently i have noticed that next to the meter pan on some new and old houses that there is a circuit breaker in line with the feed. Is this the new code? Last week i did a service upgrade which hasn't been inspected yet and i am wondering if i am going to fail.:confused:
 

iwire

Moderator
Staff member
Location
Massachusetts
Trovmar said:
This may sound like a silly question but i have to ask it anyway. Recently i have noticed that next to the meter pan on some new and old houses that there is a circuit breaker in line with the feed. Is this the new code? Last week i did a service upgrade which hasn't been inspected yet and i am wondering if i am going to fail.:confused:

The NEC has not changed but each area enforces the NEC a bit differently.

How far did you run unprotected service conductors inside the building?
 

Trovmar

Member
Location
NJ
Approximately 4 feet. They run from the meter down the side of the house maybe 2 feet and then through an LB into the circuit breaker panel.
 

iwire

Moderator
Staff member
Location
Massachusetts
Trovmar said:
Approximately 4 feet. They run from the meter down the side of the house maybe 2 feet and then through an LB into the circuit breaker panel.

You can go as far as you want outside, once you get inside the disconnecting means must be 'nearest the point of entrance'. How far that is will be up to each area. In my area 4' would be OK, some areas 15' is OK and some only allow back to back installations with no distance inside.
 

Trovmar

Member
Location
NJ
Thanks Bob, but i don't think i explained the question correctly. What i was trying to ask was why is there a circuit breaker box installed next to the meter pan on the outside of the house. Is it so you can kill the feed from the pole to work on the meter? Or is it the new requirements for the 2008 NEC.


Thanks again.
 

480sparky

Senior Member
Location
Iowegia
Sometimes it's just 'the way we do things around here.' Many areas commonly put a meter-main outside the house as SOP.
Sometimes it's a local code requirement.
Sometimes it's a POCO requirement.
Sometimes it's a building code or fire department requirement.
 

iwire

Moderator
Staff member
Location
Massachusetts
Trovmar said:
Thanks Bob, but i don't think i explained the question correctly. What i was trying to ask was why is there a circuit breaker box installed next to the meter pan on the outside of the house. Is it so you can kill the feed from the pole to work on the meter? Or is it the new requirements for the 2008 NEC.

Maybe I am still not following you. Are you sure the breaker is on the supply side of the meter?

Is this a 120/240 service?

If I see a breaker beside the meter on the outside I assume that the panel is to far inside the house to run the service conductors to without overcurrent protection.
 

Trovmar

Member
Location
NJ
Oh ok that might be it . I was curious because i only see it sometimes. I know in an apartment building were there is let's say 20 apts, there will be 20 meters on a wall with a circuit breaker next to each one. I guess thats because the run to each apt is to long.

Thanks for your help
:smile:
 

emahler

Senior Member
You are not really explaining yourself. There is a big difference between a 1 family and a 20 unit apartment. But in your area, the code dictates whether or not you have an exterior disco on the load side of the meter. JCP&L dictates whether you have to have a disco on the line side.
What side of the meter are you talking about?
 

480sparky

Senior Member
Location
Iowegia
Trovmar said:
Oh ok that might be it . I was curious because i only see it sometimes. I know in an apartment building were there is let's say 20 apts, there will be 20 meters on a wall with a circuit breaker next to each one. I guess thats because the run to each apt is to long.

Thanks for your help
:smile:

That's called a meter stack, and is generally installed to 1. put all the meters in one place and 2. to protect the conductors as they are too long to be properly protected inside the building.

meterstack2.jpg
 

mdshunk

Senior Member
Location
Right here.
If you see 20 meters, you will often see one big disconnect before all of them to comply with the 6 disconnect rule. There will still be tenant breakers beside each meter.

There are two schools of thought with regard to this. Some people see a stack of 20 meters as 20 services, each permitted to have up to 6 disconnecting means, and they say you don't need a big disconnect ahead of the stack. Other people (like me) see 20 meters as one service, just metered 20 times, and thus needing a disconnect ahead of the whole works to comply with the 6 disconnect rule.
 

ItsHot

Senior Member
outside disconnects

outside disconnects

Outside disconnects are required in many areas. One reason is for the firefighters to kill power easily to a structure before entering the building, the other reason...so the brat kid down the road can shut off your power while you're on vacation, only to come home and find all your food in frig is rotten and inside air:mad: temp is 98!!
 

480sparky

Senior Member
Location
Iowegia
ItsHot said:
.... the other reason...so the brat kid down the road can shut off your power while you're on vacation, only to come home and find all your food in frig is rotten and inside air:mad: temp is 98!!

That's why you get a padlock! :smile:
 

mdshunk

Senior Member
Location
Right here.
480sparky said:
That's why you get a padlock! :smile:
You might get a smile out of this. I always point out the padlock hasp on outdoor equipment to the customer like it's something special. Men, particularly, ooh and aah over it. Part of selling the sizzle.
 

220/221

Senior Member
Location
AZ
The outside main is in case of a fire in the building, the firemen can quickly disconnect power.

Apparently not NEC but required in a lot of places like here (AZ)
 

ItsHot

Senior Member
car sales

car sales

mdshunk said:
You might get a smile out of this. I always point out the padlock hasp on outdoor equipment to the customer like it's something special. Men, particularly, ooh and aah over it. Part of selling the sizzle.
Marc were you ever in the car sales biz?:grin:
 

iwire

Moderator
Staff member
Location
Massachusetts
220/221 said:
The outside main is in case of a fire in the building, the firemen can quickly disconnect power.

Remove the firefighters from the earth and the NEC would still require an outside disconnect if the panel inside the house is to far inside.
 