Have an existing commercial building with 240VAC, 3 phase delta, 200 amp service (in addition to 120/240 service). Three phase motor loads are excessive now and they want to expand. Service comes in through meter to 200 amp disconnect, then to 200 amp MBP, then (via 3/0 Cu, THHN in EMT) from MBP to 600 amp MLO panel.
If 240 service is increased to 400 amps and a new fused disconnect replaces the existing 200 amp disconnect, can a parallel EMT with 3/0 Cu, THHN, run from the new disconnect to the existing 600 amp MLO panel?
Per 310.10(H)(2) and (3), it looks allowed, but how precisely must lengths match?
Any other issues with paralleling?
If 240 service is increased to 400 amps and a new fused disconnect replaces the existing 200 amp disconnect, can a parallel EMT with 3/0 Cu, THHN, run from the new disconnect to the existing 600 amp MLO panel?
Per 310.10(H)(2) and (3), it looks allowed, but how precisely must lengths match?
Any other issues with paralleling?