Generally speaking, no !
That "definiton" might fit a number of underground service installs as to POCO or the customer being responsible for a certain scope of the wiring. but the NEC states:
Service Conductors. The conductors from the service point to the service disconnecting means.
generally meaning all condcutors ahead of the service disconnect, on both sides of the meter, are Service Conductors