service wire calculations

Status
Not open for further replies.

robert1234

Member
Location
edinburg texas
If I have 5 different disconnects connected to one gutter box adding to 1200 Amps. How would the service wire be sized if its from the gutter box to a step down transformer 208/120v 3-PHASE mounted on concrete pad? The conductors will run underground in a conduit. Looking at table 310.15(B)16 under the 75 degree C column it only goes to 665 Amps. WHAT TABLE AND COLUMN SHOULD BE USED HERE?
WHERE CAN THIS BE FOUND IN THE NEC BOOK.

Can it be sized like this? :
3 RUNS OF 4#600 KCMILS, 1#3/0 , 4"C

WHERE EACH PHASE WILL HAVE 3 CONDUCTOR OF 600 KCMIL AND NEUTRAL WILL ASLO HAVE 3 600 KCMIL WIRE. GROUND WILL HAVE 1 #3/0 WIRE.

 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Sure you can parallel the runs but make sure you know the rules to parallel -- 310.10(H).

What you have setup should work although I didn't calculate the pipe size.

Normally one runs a full boat in each conduit but there are circumstances where you can run all of one phase in each conduit.
 

robert1234

Member
Location
edinburg texas
If I have 5 different disconnects connected to one gutter box adding to
1200 Amps
. How would the service wire be sized if its from the gutter box to a step down transformer 208/120v 3-PHASE mounted on concrete pad? The conductors will run underground in a conduit. Looking at table 310.15(B)16 under the 75 degree C column it only goes to 665 Amps. WHAT TABLE AND COLUMN SHOULD BE USED HERE?
WHERE CAN THIS BE FOUND IN THE NEC BOOK.

CORRECTION -->
Can it be sized like this? :
1
RUN OF 4#600 KCMILS, 1#1, 4"C
WHERE EACH PHASE WILL GET 400A TO TOTAL THE 1200A
 

Malywr

Senior Member
Location
New Jersey USA
I think you are correct check article 250.122F , 310.15B16 , Table C.9 but increase size of conduit if you can so would be easier to pull cables.
 
If these 5 disconnects are service disconnects, the common conductors can be sized to the load, they need not be sized to the sum of the disconnects. Unless these are feeder taps, it's not really clear, then you have to look at the tap rules and the ocpd protecting the feeder.
 