robert1234
Member
- Location
- edinburg texas
If I have 5 different disconnects connected to one gutter box adding to 1200 Amps. How would the service wire be sized if its from the gutter box to a step down transformer 208/120v 3-PHASE mounted on concrete pad? The conductors will run underground in a conduit. Looking at table 310.15(B)16 under the 75 degree C column it only goes to 665 Amps. WHAT TABLE AND COLUMN SHOULD BE USED HERE?
Can it be sized like this? :
3 RUNS OF 4#600 KCMILS, 1#3/0 , 4"C
WHERE EACH PHASE WILL HAVE 3 CONDUCTOR OF 600 KCMIL AND NEUTRAL WILL ASLO HAVE 3 600 KCMIL WIRE. GROUND WILL HAVE 1 #3/0 WIRE.
WHERE CAN THIS BE FOUND IN THE NEC BOOK.
Can it be sized like this? :
3 RUNS OF 4#600 KCMILS, 1#3/0 , 4"C
WHERE EACH PHASE WILL HAVE 3 CONDUCTOR OF 600 KCMIL AND NEUTRAL WILL ASLO HAVE 3 600 KCMIL WIRE. GROUND WILL HAVE 1 #3/0 WIRE.