Service wire size

Status
Not open for further replies.

electricalist

Senior Member
Location
dallas tx
If you have a 200 amp meter base and 3/0 wire feeding a 200 amp OCPD.
When you do a line side tap to a 60 amp disconnect for the PV system,do the service conductors need to be rated for 260 amps?


Sent from my iPhone using Tapatalk
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
If you have a 200 amp meter base and 3/0 wire feeding a 200 amp OCPD.
When you do a line side tap to a 60 amp disconnect for the PV system,do the service conductors need to be rated for 260 amps?


Sent from my iPhone using Tapatalk

No. The PV system is a source, not a load. Output from it reduces the current in the service conductors; it doesn't increase the current.
 

Carultch

Senior Member
Location
Massachusetts
I may be looking at it wrong but it takes 60 amps to power the system I viewed it as a load


Sent from my iPhone using Tapatalk

It will take power to operate a PV system, but nowhere near its full ampere rating This is usually less than 100W per inverter, for typical string inverters.

The 60A maximum that an inverter will produce, is current that will come from the inverter to the grid. The grid and building loads are the load for the inverter.

While it is true that there is a section of conductor from your tap point to the building loads main disconnect that could conceivably be subject to 260A, the 200A main OCPD will trip before this happens. This is why if you tap on the load side of the main disconnect, you need an additional OCPD downstream of your tap point.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
I may be looking at it wrong but it takes 60 amps to power the system I viewed it as a load


Sent from my iPhone using Tapatalk
It's not a load, it's a source, and current cannot flow both directions at once. If your loads are drawing 200A and your inverter is producing 60A, the current in your service conductors is 140A, not 260A.
 