Hey there, I'm a fairly new electrician trying my hand at some residential, after working mostly industrial.

I need to run some direct bury cable from a meter 200ft to the panel in a cabin. I'm coming up with 2/0 copper that I'll need to stay in voltage drop tolerance. Just wanted to double check to make sure that's correct.

Thanks!
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
With #2/0 copper you could put in a 200 amp service. VD compensation is this case is optional but if you ran the numbers then you should be good to go.

Welcome to the Forum. :)
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
You're going to have to give a lot more detail as to the calculated load per article 220, what size service, what is the actual distance you're figuring the VD at, etc....

Your question is something like asking if 14" tires will work on your car.
Without giving the particulars a correct answer is unlikely.

Roger
 

NewbieElec

Member
Location
Alaska
I apologize for the fuzzy details. I just went to the site today to check it out for myself. The current service drop is about 200ft from the house and is 100A. I will be installing new service equipment at the pole to supply both the house and cabin. The total distance from the meter at the service drop to the cabin is 350ft direct buried. I'll be installing a disconnect on the side of the cabin which will then stub into the panel inside. The service for the cabin will be 100A.

So i'm plugging in these numbers:

(2 * 350ft * 100A * 10.7) / (120v *.03) = 208,055cm

So I'm coming up with #4/0 (211,600cm) that I will need from the Meter to the Disconnect. I feel like that is too big, but am unsure what I am doing wrong.

Thanks
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I apologize for the fuzzy details. I just went to the site today to check it out for myself. The current service drop is about 200ft from the house and is 100A. I will be installing new service equipment at the pole to supply both the house and cabin. The total distance from the meter at the service drop to the cabin is 350ft direct buried. I'll be installing a disconnect on the side of the cabin which will then stub into the panel inside. The service for the cabin will be 100A.

So i'm plugging in these numbers:

(2 * 350ft * 100A * 10.7) / (120v *.03) = 208,055cm

So I'm coming up with #4/0 (211,600cm) that I will need from the Meter to the Disconnect. I feel like that is too big, but am unsure what I am doing wrong.

Thanks

According to my Southwire App if you used aluminum, 350', 240 volts and 100 amp load the minimum size needed for less than 3% VD is 250 kcmil aluminum. For 80 amps of load you could drop down a size to #4/0 Al. Again the VD compensation is optional.
 

NewbieElec

Member
Location
Alaska
Are you using copper or aluminum? I know you said copper in your first post, but around here, copper USE is pretty rare to find in stock. I would use aluminum, probably #2, 2/0, or 4/0 depending on the specifics.

After seeing the actual distance, I will probably use Aluminum.

According to my Southwire App if you used aluminum, 350', 240 volts and 100 amp load the minimum size needed for less than 3% VD is 250 kcmil aluminum. For 80 amps of load you could drop down a size to #4/0 Al. Again the VD compensation is optional.

Why is the VD compensation not necessary? Wouldn't that lead to problems down the line if I'm out of 5% total VD from service to branch circuits?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
After seeing the actual distance, I will probably use Aluminum.



Why is the VD compensation not necessary? Wouldn't that lead to problems down the line if I'm out of 5% total VD from service to branch circuits?

For your installation vd compensation is not required by the NEC.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
After seeing the actual distance, I will probably use Aluminum.



Why is the VD compensation not necessary? Wouldn't that lead to problems down the line if I'm out of 5% total VD from service to branch circuits?