george nicholson
Member
I requested from a landlord that was providing a tenant service an 800A 3p 208V service for a 8,000sqft catering kitchen. I was given a calculated connected load of 587amps. I was told that all motors, receptacles, and HVAC were taken at 80% of running load. Lights were taken at 100%.
The landlords electrician installed 3ea 225A panels. These are being fed with 4ea 150lf of copper 4/0THHN in 2.5" PVC. Assuming the 675A is OK and I don't agree that it is----what is the proper 225A service wire size?
I would have derated the 75c wire size and used 250MCM NOT 4/0THHN for the 225A panels. The feeders are approx 150lf long and will at best have a continuous load of 195Amps.
Who is right is 4/0 THHN OK for this 225A load or should it have been 250MCM? I questioned the electrical inspector and he says that the 4/0 does not need to be derated in this application?
The landlords electrician installed 3ea 225A panels. These are being fed with 4ea 150lf of copper 4/0THHN in 2.5" PVC. Assuming the 675A is OK and I don't agree that it is----what is the proper 225A service wire size?
I would have derated the 75c wire size and used 250MCM NOT 4/0THHN for the 225A panels. The feeders are approx 150lf long and will at best have a continuous load of 195Amps.
Who is right is 4/0 THHN OK for this 225A load or should it have been 250MCM? I questioned the electrical inspector and he says that the 4/0 does not need to be derated in this application?