200a Meter socket, disco. on outside of residence. Is there any senario that would allow SEU to be run to the panel in basement:?
200a Meter socket, disco. on outside of residence. Is there any senario that would allow SEU to be run to the panel in basement:?
What if it was piped? Never mind, then it wouldn'nt be NMC.Yes, but you would have 120 volts only not 120/240.
NM would never be allowed as service conductors. SE would be.... SER is pretty much what you will need to the sub panel.What if it was piped? Never mind, then it wouldn't be NM.
Isn't SE considered non metalic cable? It is a non metallic cable but not NM or NMCNM would never be allowed as service conductors. SE would be.... SER is pretty much what you will need to the sub panel.
Correct but when you say NMC normally you would not be referring to se cable. NMC is a type of NM cable as NM-B is also. SE is referred to as service entrance. Nomenclature will cause confusion if not properly used.Isn't SE considered non metalic cable? It is a non metallic cable but not NM or NMC