How do do figure out what size wire and conduit I need for a service that is going to need 6 100 amp meters.
So lost

As Bob stated you need to do a load calculation to and size the SEC's from there or provide conductors large enough to carry the 600 amps. Have you performed a load calculation?
 
I agree with all you really need to do a load calc. for instance if all appliances are gas in residential you'll probably get away with parallel 4/0 aluminum at 400 amp. If units are small enough you may get away with less. But a load calc. is needed. best of luck.
 