no, you could tap off the 200A main conductors with smaller, say 100A for example to each meter and disconnectWhile installing a or upgrading to 200a service with 4 individual meters. You would be required to install a 200a rated conductor to each meter, from meter to disconnect and then spply 83% if applicable, correct?
For a 100a service to each apartment yes but not if you’re requiring 200a,correct?no, you could tap off the 200A main conductors with smaller, say 100A for example to each
perhaps you could explain the setup in a little more detail. Is this a 200A service conisting of a 4 gang meter socket fed with 200A and then 4 service disconnects on the load side of the meters? OR is each meter 200A? Where is the service disconnect(s)?For a 100a service to each apartment yes but not if you’re requiring 200a,correct?
First scenarioperhaps you could explain the setup in a little more detail. Is this a 200A service conisting of a 4 gang meter socket fed with 200A and then 4 service disconnects on the load side of the meters? OR is each meter 200A? Where is the service disconnect(s)?