I have a Hangar project that is required to have a separate and dedicated power supply from the facility transformer or ahead of the main service disconnecting means for providing power to Hangar bay doors. Additionally, I was told to provide a connection for a portable generator to serve the entire building. At the moment, I am of the opinion that NEC 701 applies to the Hangar bay doors and I will need to provide separate transfer equipment for the LRS and the rest of the building. Additionally, the transfer equipment for the LRS will have to be automatic per NEC 701.5. Do you agree? The facility will be served by pad-mounted transformer approximately 50 ft away and I am to provide secondary conductors to the transformer. All transfer switches will be located adjacent to the transformer. The estimated service for the Hangar bay doors is 100A and the estimated service for the rest of the facility is 1600A. What are your thoughts on the most practical approach for implementing these requirements (e.g., two service entrance rated, circuit breaker-based transfer switches (one manual and one automatic) connected to a generator connection cabinet)?