Good morning. I hope this is the correct spot for this. I am looking at a multi family project and am being told that the underground cannot run through another unit. I have read article 230 and understand that the service cannot pass from one building to another however, it is all the same building and underground. any clarification would be helpful. Thank you
 
Good morning. I hope this is the correct spot for this. I am looking at a multi family project and am being told that the underground cannot run through another unit. I have read article 230 and understand that the service cannot pass from one building to another however, it is all the same building and underground. any clarification would be helpful. Thank you

See 230.6: conductors considered outside the building
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What are you running, service entrance conductors or feeder conductors? The latter can run through the other space.
 