I have a customer with a 60Hp, AC servo motor that has the following ratings:
Vmax = 400 V
Io = 66 A
Imax = 264 A
fn = 225 Hz
Under normal operating conditions, 60Hp is adequate to move the load, however, they want to get maximum acceleration out of the load which requires considerably more current than a 60Hp servo controller can source. As a result, they want to put a 150Hp servo controller on the motor with a peak output boost current of 234A and continuous output current of 156A. In theory, the boost current would only be applied for a fraction of a second during acceleration, but my concern is that a failure in the drive control or an unintentional change to a drive parameter could result in the controller sourcing that current for a longer period.
An additional concern is that the system is intended to be portable with the servo controller and the motor separated by 10' to 100' of individual conductors, not in conduit. The distance is within the manufacturers recommendation, but their recommended conductor size is 4/0 and we cannot fit 4/0 terminals on the motor binding posts.
The customer contends that because the boost current is of such short duration, the output wire need only be sized for the 66 A Io of the motor. My contention is that the wire must be sized based on the drive output capability for safety.
Am I correct, or paranoid?
Vmax = 400 V
Io = 66 A
Imax = 264 A
fn = 225 Hz
Under normal operating conditions, 60Hp is adequate to move the load, however, they want to get maximum acceleration out of the load which requires considerably more current than a 60Hp servo controller can source. As a result, they want to put a 150Hp servo controller on the motor with a peak output boost current of 234A and continuous output current of 156A. In theory, the boost current would only be applied for a fraction of a second during acceleration, but my concern is that a failure in the drive control or an unintentional change to a drive parameter could result in the controller sourcing that current for a longer period.
An additional concern is that the system is intended to be portable with the servo controller and the motor separated by 10' to 100' of individual conductors, not in conduit. The distance is within the manufacturers recommendation, but their recommended conductor size is 4/0 and we cannot fit 4/0 terminals on the motor binding posts.
The customer contends that because the boost current is of such short duration, the output wire need only be sized for the 66 A Io of the motor. My contention is that the wire must be sized based on the drive output capability for safety.
Am I correct, or paranoid?