SES Sizing and Step Down XFMR

Status
Not open for further replies.
Location
United States
Occupation
Electrical Engineer
Greetings All,
What size service entrance at 277/480V
3 Phase will I need to feed (15) 200AMP Panels 120/240V?

Planning for 75kVA step down transformer, would that be sufficient?

Would 100 AMP circuit breaker be sufficient?
 
So you're using a separate step down transformer for each panel? The secondaries are 3 phase, 4 wire, Delta?
 
So you're using a separate step-down transformer for each panel?
I would like to know the step-down transformer size for both options (one xfmr for each panel), and (one xfmr for all 15 panels)

The secondaries are 3 phase, 4 wire, Delta?
Yes
 
So you're using a separate step-down transformer for each panel?
I would like to know the step-down transformer size for both options (one xfmr for each panel), and (one xfmr for all 15 panels)

The secondaries are 3 phase, 4 wire, Delta?
Yes
How could we possibly say without knowing what the loads are? IF you want to know the KVA to supply a panel or panels that are loaded to their full rating, I assume that being an electrical engineer you know how to calculate that.
 
It sounds like he's interested in using the full load rating of 200 amps and calculate for either 1 or 15 transformers.
 