SES Sizing and Step Down XFMR

Merry Christmas
Location
United States
Occupation
Electrical Engineer
Greetings All,
What size service entrance at 277/480V
3 Phase will I need to feed (15) 200AMP Panels 120/240V?

Planning for 75kVA step down transformer, would that be sufficient?

Would 100 AMP circuit breaker be sufficient?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
So you're using a separate step down transformer for each panel? The secondaries are 3 phase, 4 wire, Delta?
 
Location
United States
Occupation
Electrical Engineer
So you're using a separate step-down transformer for each panel?
I would like to know the step-down transformer size for both options (one xfmr for each panel), and (one xfmr for all 15 panels)

The secondaries are 3 phase, 4 wire, Delta?
Yes
 
So you're using a separate step-down transformer for each panel?
I would like to know the step-down transformer size for both options (one xfmr for each panel), and (one xfmr for all 15 panels)

The secondaries are 3 phase, 4 wire, Delta?
Yes
How could we possibly say without knowing what the loads are? IF you want to know the KVA to supply a panel or panels that are loaded to their full rating, I assume that being an electrical engineer you know how to calculate that.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
It sounds like he's interested in using the full load rating of 200 amps and calculate for either 1 or 15 transformers.
 