Forum,
Have a question about setting the instantaneous trip setting on an MCP circuit breaker. In the past in our plant, common practice has been to dial up the trip setting as far as it'll go, but I'm convinced that this could really screw up the system coordination. The way I'm trying to teach our plant personnel is to set the instantaneous trip setting based on the kVA code for a locked rotor on the motor nameplate, using calculation. So far using this method has caused me no problems, except for now. We recently replaced a standard efficiency motor with a NEMA Premium Efficiency motor, and we could not get it to start. We ended up replacing the old breaker with a new one that has a higher inrush capability, and it started right up without a problem. What's throwing me for a loop is the locked rotor kVA code on the nameplate for both motors is the same. Can you not set instantaneous trip settings for a premium efficiency motor based on the kVA code? Let me know your thoughts. I'm starting to think I'm not getting the full picture here, and maybe the old breaker just went bad at the same time we replaced the motor. Let me know your thoughts.
Some background info:
Have a question about setting the instantaneous trip setting on an MCP circuit breaker. In the past in our plant, common practice has been to dial up the trip setting as far as it'll go, but I'm convinced that this could really screw up the system coordination. The way I'm trying to teach our plant personnel is to set the instantaneous trip setting based on the kVA code for a locked rotor on the motor nameplate, using calculation. So far using this method has caused me no problems, except for now. We recently replaced a standard efficiency motor with a NEMA Premium Efficiency motor, and we could not get it to start. We ended up replacing the old breaker with a new one that has a higher inrush capability, and it started right up without a problem. What's throwing me for a loop is the locked rotor kVA code on the nameplate for both motors is the same. Can you not set instantaneous trip settings for a premium efficiency motor based on the kVA code? Let me know your thoughts. I'm starting to think I'm not getting the full picture here, and maybe the old breaker just went bad at the same time we replaced the motor. Let me know your thoughts.
Some background info:
- Both motors are three-phase, 460v, 100hp motors, with FLA's of 113.
- Both kVA codes are G
- The old breaker was a Siemens 125A, with an inrush capability of 1250A (tripped right after pushing start)
- The new breaker is a Square D 200A, with an inrush cabability of 2000A (started the motor up just fine)