setting transfer switch for 200amp subpanel for generator backup
City Mission
New User
Facilities
can I install a transfer switch to a 200 amp sub-panel that is fed from a 600amp Main Distribution Panel to supply 200 amp subpanel only
Yes.
Is the generator sized to carry the calculated load so the generator won’t be overloaded?
Typically the generator will be wired as non SDS, and the bonding-grounding is done at the service