I am bidding on a job to install:
2 200A 1? service panels
1 100A 1? service panel
All in one building. The 200 amp panels are for 2 storefronts, the 100 amp panel is for a 2 bdroom apt over the stores. I am considering running 2 sets (2 hots, 1 neutral per set) of 4/0 CU conductors in 3" PVC to support the 500 amp capacity. In the basement I am looking to install a multi postion meter pan with 3 200 amp meter postions.
Question:
1) Must the service entrance conductors be rated for the sum of the individual service panels?
2)Is there an issue with installing a 200 amp meter hub and then having a 100 amp main? An inspector for the local POC warned me at another site that he could reject an install since I had a 200 amp meter pan and a 100 amp main breaker.
3) At the service head, can I get a multiphase head to allow 6 conductors?
Is there any other way to skin this cat?
Thanks
Re: Setting up multiple service panels
No, they are only required to be rated equal or greater than the calculated load.
Not a NEC issue but it could be a power company requirement.
Yes.
By the way, two sets of 4/0s only results in 460 amps if in separate raceways.
Two sets of 4/0s in one raceway only results in a capacity of 416 amps.
[ April 26, 2005, 04:52 PM: Message edited by: iwire ]
Thanks Bob,
I did not account for derating w/more than 3 conductors in conduit. But when I do can't I derate the 250A rating for 4/0 CU at 80%?
500 x 80% =400??
310.15b is for dwelling services / feeders
but you can use 310.16 (260a for derating purposes only)(90 deg column)
Table 310.16 is for "Not More Than Three..."
Should I use values from table 310.17 to derate since there will be 4 current carrying conductors in the conduit?
Coppertree, No relation that I know of.
Jjhoward, Table 310.17 is for conductors in free air. You should use table 310.16 90 deg column for derating.
Jim