338.10 Uses Permitted.
(A) Service-Entrance Conductors. Service-entrance cable
shall be permitted to be used as service-entrance conductors
and shall be installed in accordance with 230.6, 230.7, and
Parts II, III, and IV of Article 230.
(B) Branch Circuits or Feeders.
(1) Grounded Conductor Insulated. Type SE service-
entrance cables shall be permitted in wiring systems
where all of the circuit conductors of the cable are of the
thermoset or thermoplastic type.
(2) Use of Uninsulated Conductor. Type SE service-
entrance cable shall be permitted for use where the insu-
lated conductors are used for circuit wiring and the uninsu-
lated conductor is used only for equipment grounding
purposes.