Hendrix
Senior Member
- Location
- New England
I thought that service cable can not be concealed. Can someone point me to that?
But then it needs to be protected according to 230.50(B) no?SE cable may be concealed or exposed.
The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.
Yes where it is subject to damage-- that is a very subjective statement. Thru the back of a meter and down to a cellar panel IMO does not need protection- no different than NM cable entering the top of a panel.But then it needs to be protected according to 230.50(B) no?
But........it isn't fused and running concealed behind sheetrock :?Yes where it is subject to damage-- that is a very subjective statement. Thru the back of a meter and down to a cellar panel IMO does not need protection- no different than NM cable entering the top of a panel.
Yep and that is why the distance is restricted. Some areas have an actual distance they allow once it enters the building. I was visualizing thru the wall and right into a panel. Can you not pipe it as I stated above.But........it isn't fused and running concealed behind sheetrock :?
But........it isn't fused and running concealed behind sheetrock :?
Our restrictions are 15' as the crow flies.Yep and that is why the distance is restricted. Some areas have an actual distance they allow once it enters the building. I was visualizing thru the wall and right into a panel. Can you not pipe it as I stated above.