Hello, recently I did an electrical project for a gym and I connected 3 air handling units in the same circuit (2.5 A each, 208 V, single phase) I used a 2P-15 A breaker (to comply whith 430-53 a)) and a disconnect at each unit.
The AHJ says this is against code, that you must comply with art 440 and not with 430, what do you think? I have done this before and in an another project and the AHJ (different to this) didn´t say anything about it.
Thanks
Tom
The AHJ says this is against code, that you must comply with art 440 and not with 430, what do you think? I have done this before and in an another project and the AHJ (different to this) didn´t say anything about it.
Thanks
Tom