I will try and be concise. I am moving a cord drop for a band saw which shares a circuit with another band saw and a hoist. Saw #1 has a FLA of 10.2 for the entire machine. Saw #2 is 9.7 FLA for the whole machine. These both have other components other than just the saw motors. The hoist is 1hp and has a nameplate of 3.5A @ 240V. They are all currently wired with #14s from a 240v 3 phase fuse panel with 15A fuses on that ckt. The saws branch (tap) off in a junction box to the individual cord drops and the hoist goes to a fused (15A) disconnect and then is hard wired. I believe 430.24 Exception #1 comes into play for sizing the conductors. I don't understand the last part "or the largest continuous..." They are never or very rarely running at the same time due to the lay out of the room (its very small) it just seems to me that #14 wire is too small. Does 430.28 come into play too? Sorry I wasn't concise. Take it easy on me this is my first post.