Sevice riser

Status
Not open for further replies.

fittowork1

Member
Location
hayward ca
Occupation
contractor
I have a meter pack that was ordered wrong by another contractor and I am forced to come out the bottom with a overhead service

Near the panel is the gas meter to the left in-between the meter pack and the weather head point


My issue is getting the conduit back up the wall and staying away from the gas meter


Does 3 foot rule apply to the service conduit spacing away from the gas meter

Also I have to run accross the eve to a 90 sweep keeping the coupling below the roof line with a strap above the coupling

Am I out of my mind or is this possible 20220601_160308.jpg
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
AFIK the gas meter is irrelevant
The local gas company (for me and the OP) doesn't think so. And since they are also the POCO (PG&E), they can enforce that easily.

Per the diagram below from their service manual (called the Green Book), they want you to generally stay 3' away from the point where the gas service rises out of the ground. The exception is that conduit shown; note 3 says that the section in the grey area must be continuous without joints, fittings, etc. and at least 6' above the gas regulator vent.

Cheers, Wayne

Capture.JPG
 
Last edited:

jap

Senior Member
Occupation
Electrician
Isn't this an extension of a previous post on "entering the side of a meter pack" ??

JAP>
 

fittowork1

Member
Location
hayward ca
Occupation
contractor
The local gas company (for me and the OP) doesn't think so. And since they are also the POCO (PG&E), they can enforce that easily.

Per the diagram below from their service manual (called the Green Book), they want you to generally stay 3' away from the point where the gas service rises out of the ground. The exception is that conduit shown; note 3 says that the section in the grey area must be continuous without joints, fittings, etc. and at least 6' above the gas regulator vent.

Cheers, Wayne

View attachment 2560842
Thanks Wayne

But I looked at pacific gas and electrics green book and it has no diagram like that. I'm in norther California. Maybe I missed it It has one but with no conduit
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
But I looked at pacific gas and electrics green book and it has no diagram like that. I'm in norther California. Maybe I missed it It has one but with no conduit
I got the current Green Book from here:


The image I posted is Figure 2-19 on page 2-32, in Chapter 2 "Gas Services". Figure 5-3 on page 5-14 in Chapter 5 "Electric Metering: General" appears identical.

Maybe you're looking at an older version?

Cheers, Wayne
 

fittowork1

Member
Location
hayward ca
Occupation
contractor
I got the current Green Book from here:


The image I posted is Figure 2-19 on page 2-32, in Chapter 2 "Gas Services". Figure 5-3 on page 5-14 in Chapter 5 "Electric Metering: General" appears identical.

Maybe you're looking at an older version?

Cheers, Wayne
Ya I was looking at an old version I defiantly do not remember that conduit rule last edition of the Green Book

Thanks
 

fittowork1

Member
Location
hayward ca
Occupation
contractor
Meters Hub, straight up through the soffit riser. Guy as needed.
I would love to but this panel was ordered and installed a year before I took this project over and it's specs are for bottom entry only

If it was a 200 dollar panel I would start over but 4 meter packs are expensive

Also if I go straight up the ext poco is 25 feet away
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
What manufacture is the meter stack? I looked at Square D, Siemens and Eaton and they are all listed as suitable for overhead or underground feed?

How much extra conduit and wire will it take to loop into the bottom? If the meter stack you have is really not able to be fed overhead you would probably better off replacing it. Have you priced 3" conduit and 600CU? Probably looking at at least $75 per foot material.
 

fittowork11

Member
Location
hayward ca
Occupation
contractor
The local gas company (for me and the OP) doesn't think so. And since they are also the POCO (PG&E), they can enforce that easily.

Per the diagram below from their service manual (called the Green Book), they want you to generally stay 3' away from the point where the gas service rises out of the ground. The exception is that conduit shown; note 3 says that the section in the grey area must be continuous without joints, fittings, etc. and at least 6' above the gas regulator vent.

Cheers, Wayne

View attachment 2560842
thanks wayne you saved me a major headache
 

fittowork11

Member
Location
hayward ca
Occupation
contractor
Why can't you use a Myers Hub and come out of the top of the meter base?
I actually was going to do that and I consulted with the shop that the panel was purchased from and the panel specs specify bottom entrance only not trying to put a hole in the top then get called on it
 