I found a discussion from back in 2007 about a Sewage Pumping Station Wet Well. The discussion is linked below.
http://forums.mikeholt.com/showthread.php?t=91513
I'm not an Electrical Engineer and was hoping someone could clarify what was discussed in that thread. The NEC 501.15(B)(2), Exception 2 what applies for an open air termination for an explosive environment?
We are trying to install a quick disconnect panel that us Meltric plugs next to our pump station wet well. The power and control cables will run first to a concrete vault. The wet well and the vault will be located directly next to each other with less than a foot of 12"dia pvc sch pipe in between. The concrete vault top will be half grate and grated stand for the panel. The power and control cables will run through the wet well to the vault through the grated stand to the bottom of the panel.
We have been having a discussion with our electrical engineer about this item. He says the code is very clear that you need a seal off when leaving an explosive environment. We would like to avoid a seal off because they would make the Meltric plug useless. Would the grated control panel stand be adequate to meet NEC 501.15(B)(2), Exception 2?
Thanks
http://forums.mikeholt.com/showthread.php?t=91513
I'm not an Electrical Engineer and was hoping someone could clarify what was discussed in that thread. The NEC 501.15(B)(2), Exception 2 what applies for an open air termination for an explosive environment?
We are trying to install a quick disconnect panel that us Meltric plugs next to our pump station wet well. The power and control cables will run first to a concrete vault. The wet well and the vault will be located directly next to each other with less than a foot of 12"dia pvc sch pipe in between. The concrete vault top will be half grate and grated stand for the panel. The power and control cables will run through the wet well to the vault through the grated stand to the bottom of the panel.
We have been having a discussion with our electrical engineer about this item. He says the code is very clear that you need a seal off when leaving an explosive environment. We would like to avoid a seal off because they would make the Meltric plug useless. Would the grated control panel stand be adequate to meet NEC 501.15(B)(2), Exception 2?
Thanks