Does anyone know the general distance a sewer line should be separated from the feeder conduits entering the MSB from underground?

Sent from my SM-N910T using Tapatalk
You revived an old thread by posting a new topic within it. You really should start a new thread with your new topic.
 
NEC has no seperation requirement on the piping itself as long as you comply with the 110.26 rules in regard to the switchgear. There may be local or Power Co. (if they are actually service conduits) to consider.
 