Sewer line over panel allowed?

Status
Not open for further replies.

hawkeye

New member
Can you have a septic line directly above the main panel box? This would mean that the sink is above the panel as well, making for a possible water leak if it would ever happen.
 
Re: Sewer line over panel allowed?

Do you mean that the main panel is in a room below a bathroom? Are you concerned about the bathroom sink overflowing on to the bathroom floor, and then going through the basement ceiling and falling onto the panel? I don't think the rules cover that, so it would not be a violation.

But a pipe above a panel is not a violation, unless it is within the working space set aside by 110.26.
 
Re: Sewer line over panel allowed?

110.26(F)(1)(b) Foreign Systems. The area above the dedicated space required by 110.26(F)(1)(a) shall be permitted to contain foreign systems, provided protection is installed to avoid damage to the electrical equipment from condensation, leaks, or breaks in such foreign systems.
If the bathroom floor achieves this protection, then I don't see a problem with the pipes above the panel that are on the floor above, or the floor above that, or the floor above that, or the floor above that, etc.

Jim
 
Re: Sewer line over panel allowed?

110.26(F)(1)(a)

This applies to indoor

Dedicated Electrical Space. The space equal to the width and depth of the equipment and extending from the floor to a height of 1.8 m(6 ft) above the equipment or to the structural ceiling, whichever is lower, shall be dedicated to the electrical installation. No piping, ducts, leak protection apparatus, or other equipment foreign to the electrical installation shall be located in this zone.

Exception: Suspended ceilings with removable panels shall be permitted within the 1.8-m (6-ft) zone.

[ August 26, 2005, 04:15 PM: Message edited by: physis ]
 
Re: Sewer line over panel allowed?

This issue pops up all the time during our inspections.
The Floor is structural - so if the pipes and sink are above the floor it is not a code violation.

On the other hand if the pipe is above the "footprint" of the panel (and below the structural ceiling) and less than 6 feet above the panel, it is a violation of 110.26(F)(1)(a). Simply installing a drip pan is not sufficient if the pipe is not above the 6 ft zone.

"(F) Dedicated Equipment Space. All witchboards, panelboards, distribution boards, and motor control centers shall be located in dedicated spaces and protected from damage.

Exception: Control equipment that by its very nature or because of other rules of the Code must be adjacent to or within sight of its operating machinery shall be permitted
in those locations.

(1) Indoor. Indoor installations shall comply with 110.26(F)(1)(a) through (d).
(a) Dedicated Electrical Space. The space equal to the width and depth of the equipment and extending from the floor to a height of 1.8 m (6 ft) above the equipment or to the structural ceiling, whichever is lower, shall be dedicated
to the electrical installation. No piping, ducts, leak protection apparatus , or other equipment foreign to the electrical
installation shall be located in this zone.
Exception: Suspended ceilings with removable panels shall be permitted within the 1.8-m (6-ft) zone.
(b) Foreign Systems. The area above the dedicated
space required by 110.26(F)(1)(a) shall be permitted to contain foreign systems, provided protection is installed to avoid damage to the electrical equipment from condensation,
leaks, or breaks in such foreign systems.
 
Re: Sewer line over panel allowed?

Thank you Romeo, but I just typed in the code.

I have to thank Jim cause I couldn't remember where to find it.
 
Re: Sewer line over panel allowed?

What do you guys think of this one?
PanelunderTub.jpg
 
Re: Sewer line over panel allowed?

I think that 110.26 Says

Spaces About Electrical Equipment. Sufficient access and working space shall be provided and maintained about all electric equipment to permit ready and safe operation and maintenance of such equipment.

Then (F), a subsection of 110.26, says:

Dedicated Equipment Space. All switchboards, panelboards, distribution boards, and motor control centers shall be located in dedicated spaces and protected from damage.

I think that 110.26(F) is outside the scope of 110.26 with regard to protecting equipment outside of where working space is required.
 
Re: Sewer line over panel allowed?

Angles of pictures are always hard to tell, but if that trap is in the "footprint" of the panel directly below it, this would be a violation of 110.26(F)(1)(a) - even as unusual as this installation is.

Ryan is this picture from an inspection you did?

This work looks like modification to some older work.
 
Re: Sewer line over panel allowed?

Let me ask what the opinion would be if this "offending" component weren't a plumbing pipe, but instead, a fire break.

Still a violation of 110.26(F)(1)(a)?
 
Re: Sewer line over panel allowed?

Sam,
If you apply the wording of that rule as written, you can't install a recessed panel!! Only surface panels are permitted.
Don
 