Rich S.
Member
- Location
- long beach ca
I am working with a Sewer Lift station that has recently Installed Two out of Four New Dry pit submersible pumps. They are installed in a dry pit application. Our problem is the new pumps are getting super hot you can fry an egg on the motor. They can run from 3 to 4 hours at a time due to the volume coming into the station. The pump name plate says:
DUTY continuous/submerged
15 min. per hr./Air
The other issue Issue is these two pumps have a VFD drive and which we don't use them for this application so we have them switched to By-Pass mode. I was told that by having these in a by pass mode does something with the power factor which calculates I believe around .68 and should be closer to 1.0. By installing a capacitor this will bring the PF closer to 1.0 and the pumps will run cooler and by having the PF at that number of .68, the pumps are running under voltage creating them to heat up. We also checked the volt readings on the pumps with and with out a load and they are in the normal range. Could I have two problems. PF and wrong pump application. The older pumps. No VFD, No Heat, No problem. Any help?:?
DUTY continuous/submerged
15 min. per hr./Air
The other issue Issue is these two pumps have a VFD drive and which we don't use them for this application so we have them switched to By-Pass mode. I was told that by having these in a by pass mode does something with the power factor which calculates I believe around .68 and should be closer to 1.0. By installing a capacitor this will bring the PF closer to 1.0 and the pumps will run cooler and by having the PF at that number of .68, the pumps are running under voltage creating them to heat up. We also checked the volt readings on the pumps with and with out a load and they are in the normal range. Could I have two problems. PF and wrong pump application. The older pumps. No VFD, No Heat, No problem. Any help?:?