Not sure if this is the place or Campfire Chats but here goes.
I am surprised that we have not heard of any reports from our members in the SF bay area regarding the massive
power outage last Friday 4-21 in San Francisco. It was reported that the outage that included parts of the city from the financial district to the Sunset (west coast) were affected to the tune of approx 90K customers. A circuit breaker burnt up in the POCO's Larkin & Eddy St substation. This old equipment was scheduled for replacement in the near future.
We were called out that morning on reports that a Telco office had lost power and some backup equipment failed. The emer gen started and at the house service panel the telco breaker pair transferred ok but the building power circuit failed. The utility breaker opened but the emergency breaker failed to close. After about 45 min. the gen shut down on high temp alarm since the cooling fans were feed from the building power circuit so the whole office was dead, Telco equip on batteries. The UPS that fed the emer lights eventually died and it was all flashlights from there.
We could not get the BP breaker (1600A W SPB-100) to close and had to replace it with a spare: top cell and no breaker lifting cradle!
Had to change the belts on the air compressor motors to the backup DC motor to get the air start tanks filled to start the gen to get emer power back to the bldg. At around 5PM POCO power came back and got the office back to normal. An exciting day to say the least!
I am surprised that we have not heard of any reports from our members in the SF bay area regarding the massive
power outage last Friday 4-21 in San Francisco. It was reported that the outage that included parts of the city from the financial district to the Sunset (west coast) were affected to the tune of approx 90K customers. A circuit breaker burnt up in the POCO's Larkin & Eddy St substation. This old equipment was scheduled for replacement in the near future.
We were called out that morning on reports that a Telco office had lost power and some backup equipment failed. The emer gen started and at the house service panel the telco breaker pair transferred ok but the building power circuit failed. The utility breaker opened but the emergency breaker failed to close. After about 45 min. the gen shut down on high temp alarm since the cooling fans were feed from the building power circuit so the whole office was dead, Telco equip on batteries. The UPS that fed the emer lights eventually died and it was all flashlights from there.
We could not get the BP breaker (1600A W SPB-100) to close and had to replace it with a spare: top cell and no breaker lifting cradle!
Had to change the belts on the air compressor motors to the backup DC motor to get the air start tanks filled to start the gen to get emer power back to the bldg. At around 5PM POCO power came back and got the office back to normal. An exciting day to say the least!