stockhatch
I have a sample question booklet with this question in it:
A single family dwelling has 3200 sq ft, and the following equipment:
15,000 VA fixed space heater at 240v
14,000 VA range at 240v
6,000 VA dryer at 240v
1,000 VA disposal at 120v
1,500 fan motor at 120v
Two, non-motor, 120v, non-fastened appliances with a total nameplate rating of 4,500 VA
Using the standard method of calcualtion, determine the dwellings total load.
I figured this:
3200 sq ft X 3 VA = 9600 VA
+ 4,500 VA for 2 small appliances and washer = 14,100 VA
3,000 VA at 100% = 3,000 VA
remaining 11,100 at 35% = 3,885 VA
total general of 6,885 VA
heat = 15,000 VA at 100% = 15,000 VA
appliances = 4,500 VA at 100% = 4,500 VA
add disposal at 100% 1,000 VA ?
add blower motor @ 100% VA = 1,500 VA ?
add dryer at 100% = 6,000 VA
add range at 8,800 VA (14,000 = 8,000 VA + .10% correction due to two points over 12KW rating)
TOTAL = 43,685 VA ?
The book answer is 43,935 VA and I cant figure out why. Is there something I am missing regarding the fan motor and disposal loads? Is it something else I am missing, or is the book wrong?
Thanks in advance.
I figured this:
TOTAL = 43,685 VA ?