Advances in semiconductors 
and power electronics technologies 
have made adjustable-
speed drives (ASDs) with 
pulse-width modulation 
(PWM) technology a popular 
choice for many motor-driven 
processes. Originally, ASDs 
with PWM inverters had 
switching rates between 1 and 
8 kHz. To eliminate the audible 
motor noise caused by such 
low switching frequencies, 
manufacturers developed ASDs 
with switching frequencies as 
high as 20 kHz. The faster 
switching frequencies did 
reduce motor noise, but they 
also created a side effect: 
excessive motor-shaft voltage 
and current that can discharge across the motor bearings. 
ASDs that use insulated-gate bi-polar transistors (IGBTs) as high-frequency switches are most 
likely to cause bearing-discharge current. The high switching frequency and fast rise times of an 
IGBT inverter output can cause induced voltage in the rotor to be capacitively coupled to the 
motor shaft. As shown in Figure 1, this shaft voltage can exceed the dielectric strength of the 
lubricant in the shaft bearings. The resulting current flows from the shaft, through the bearing 
lubricant, and to the grounded motor frame, pitting?or fluting?the bearing races. The resulting 
high rolling resistance leads to premature failure of the shaft bearings. This PQTN Application 
provides ASD users with some pragmatic insights into the nature of the problem caused by 
bearing discharge currents and suggests preventive or corrective actions to avoid the problem. 
What To Look For: 
Audible motor noise and vibration are usually the first obvious symptoms of premature bearing 
failure. Because excessive noise and vibration can be symptoms of other motor problems, 
maintenance personnel frequently misdiagnose problems caused by fluting. Usually, the current 
arcing across the bearings will first damage the smaller idle bearing opposite the end of the shaft 
connected to the motor load. Idle-bearing failure can occur as soon as six months after the motor 
has been installed. 
Discharge current may also damage the bearings of other equipment connected to the motor 
shaft, such as direct-connected tachometers and gear boxes. In many cases, discharge current will 
damage the tachometer bearings instead of the motor bearings because the smaller tachometer 
bearings offer the path of least resistance. Damaged tachometer bearings can cause the tachometer 
to vibrate, resulting in an erratic signal from the tachometer. 
A shaft voltage as low as six volts can cause arcing through the bearing lubricant, depending 
upon the type of bearing lubricant and the clearing between the race and the ball bearings. 
Excessive shaft voltage can be verified in two ways. One way is to measure the shaft-to-ground 
voltage, which requires a specialized shaft-monitoring device. If motor bearings have already 
failed, then inspect the bearing races for fluting. If the bearing races look similar to those in 
Figure 2, and the ASD driving the motor is a PWM-type with a switching frequency above 
10 kHz, then most likely the shaft voltage is excessive. 
HOW TO PREVENT PREMATURE BEARING FAILURES 
Install a Shaft Grounding System Minimizing the 
magnitude of the shaft voltage reduces the chance of 
electrical arcing through bearing lubricant. Grounding 
the motor shaft with a system of brushes creates a low-
impedance path to ground for otherwise damaging 
discharge currents. A number of brush systems are 
commercially available. Soft carbon brushes are 
usually not suitable because they may create a nonconductive 
film that prevents electrical contact between 
the brushes and shaft. Brushes made of special materials?
such as brass and stainless steel?do not create 
this film. Also, a sealed grounding system is recommended 
for a clean-room environment, which may be 
contaminated by airborne particles from a standard 
grounding-brush system. During every routine maintenance, 
ensure that the brushes are in electrical contact 
with the shaft, regardless of the type of grounding 
system you select. 
Install Insulated Motor Bearings - Although insulated 
motor bearings stop the flow of discharge current 
through the motor bearings, they do not prevent damage 
to the bearings of other shaft-connected equipment, 
such as tachometers and fans. Also, the voltage 
on the shaft of a motor with insulated bearings and 
without shaft-connected equipment may pose a risk of 
a mild shock to anyone who touches the rotating shaft. 
Decrease the ASD Switching Frequency - The 
switching frequency of most PWM ASDs can be set by 
the operator. By decreasing the switching frequency of 
an existing ASD, you can prevent the premature failure 
of motor bearings. Although shaft voltages will be 
Quick Check List 
-Look for signs of premature bearing failure such 
as audible motor noise, vibration, and localized 
heating. 
 
-Look for fluting in the races of damaged 
bearings from motors and other shaft-
connected equipment such as tachometers, 
pumps, fans, and gear boxes. 
 
-Reduce shaft voltage by installing a shaft 
grounding system. 
 
-Stop current from discharging through motor 
bearings by replacing existing motor bearings 
with insulated bearings or decreasing the 
switching frequency of the ASD that drives the 
motor. 
 
-Purchase new motors with bearings guaranteed 
against premature bearing failure. 
present at lower switching frequencies, industry 
experience to date indicates that problems caused by 
discharge current begin mostly when the ASD switching 
frequency is greater than 10 kHz. Therefore, if 
shaft grounding systems or insulated bearings are impractical 
options, then avoid using switching frequencies 
above 10 kHz. If a higher switching frequency 
must be used, then purchase motors with warranties 
against bearing failure caused by discharge current.