14/2 AC cable with the connector on the outside of the box.
Would it have to be stamped in the canopy? I’ve never seen it on any of the lights.Keep in mind that if you are using a luminaire that has a canopy with a marked fill in cubic inches you can use that for additional conductor fill. See 314.16(A).
Chris
Would it have to be stamped in the canopy? I’ve never seen it on any of the lights.
Keep in mind that if you are using a luminaire that has a canopy with a marked fill in cubic inches you can use that for additional conductor fill. See 314.16(A).
Chris
Yes, it must be stamped on the fixture..
314.16(A) says this:Where does it say that in the code?
314.16(A) Box Volume Calculations. The volume of a wiring enclosure (box) shall be the total volume of the assembled sections and, where used, the space provided by plaster rings, domed covers, extension rings, and so forth, that are marked with their volume or are made from boxes the dimensions of which are listed in Table 314.16(A).
314.16(B)(1)Exception: An equipment grounding conductor or conductors or not over four fixture wires smaller than 14 AWG, or both, shall be permitted to be omitted from the calculations where they enter a box from a domed luminaire or similar canopy and terminate within that box.
Close; see 314.16(B)(1) exception.