electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
Consider the following situation. I have a POCO secondary vault/handhole that has two ground rods installed per POCO specs. I do not see any NEC requirement for these rods at the vault, except possibly 250.24(A)(2). About 5 feet away from the vault, I have a temp power pole. Should the GEC for the temp pole be connected to one of the vault rods or have its own rod? I dont really like using the same rods for both because I then I parallel the neutral conductor between the handole and the temp pole. But I also dont like have two pieces of metallic equipment using different GES's and being in such close proximity (Yes they are each bonded to the neutral conductor). It seems to me the best thing would be to have just a single GEC, but I cant skip the vault connection due to POCO specs and I cant skip the one at the service disconnect per NEC.