Re: Shared Circuits on single pole breakers
This is something that I am surprised the code does not address. When using stranded wire we have found that the type of clamping can be important. For example, if the wire is held only by the clamping effect of a terminal screw, stranded wire does not hold very well. It tends to flair out, especially if it is not twisted, and this forces some of the wire strands out from under the screw head. When this happens, one has effectively reduced the wire size at the terminal point and these can heat up. We now require saddle strap type terminals when using stranded wire on our products. When using solid core wire, I have experienced situations where the wires were not laid side-by-side under a saddle strap type terminal (they were crossed so that one was on top of the other). Over time, the two wires managed to slide off each other and the result was a loose connection, which resulted in an overheated wire connection. I usually try to avoid multiple wires under one terminal unless I use a saddle strap type terminal and place one wire on each side of the terminal's screw. This way, I am limited to a maximum of two wires and each is equally clamped under the strap. At least as equally as possible.
Bob