McCElectric
Member
- Location
- Pennsylvania
- Occupation
- Electrician
Chasing down issues in new addition to building related to grounding, and harmonic issues. Discovered the Emergency lighting panel (ELP) that is fed from a panel in original building thats connected to back up power, has some neutrals tied together with our normal lighting panel (L1). This was discovered by reading V,I,R of the MDS feeding the addition with the power off. Another test was then done between the panels, if you remove ELP phase A circuit 1 neutral, turn the circuit off and turn it back on, if it stayed on it was a culprit, then we did same process with LP circuits till ELP phase A circuit 1 turned of the lights. Then we investigated for the spot they could potentially be tied together. We located two spots and cleared 2 circuits from ELP that were tied to LP1. We had 6 drivers go bad by the time we found the shared neutrals also lost 3 smart switches. I originally thought maybe they acted like a MWBC and went into series and those drivers got smoked, but there was always one neutral landed during the test except when we would turn a circuit back on with no neutral. The engineers were convincing it would be like opening a switch, the lights just won’t work. My other theories are these drivers can be damaged with over voltage or even under voltage, or the drivers could short out to ground, due to the test.
ELP 3 phase 277/480
LP 3 phase 277/480
One spot was same phase
One spot was different phases
ELP 3 phase 277/480
LP 3 phase 277/480
One spot was same phase
One spot was different phases